I would need a group to execute:
- on value change of a certain tag
- and when a trigger becomes active
Is there a way to achieve this?
Setup a transaction group to trigger on a tag
Setup a tag change gateway or Client script that sets a tag hi or low based on its value
Have the transaction group trigger on that tag
Two Tags:
– Test Tag: Value you are looking to see change
– Trigger Tag: External trigger.
Run Always Expression Items:
– Compare Value: Holds previous value
– Group Trigger: Triggers the Group.
Triggered Expression Items:
– Update Compare Value: When the group is executed, stores the Test Tag Value
– Reset Trigger Tag: Resets External Trigger to zero.
[attachment=1]1-22-2014 11-02-18 AM.png[/attachment]
Group Trigger expression:
[attachment=0]1-22-2014 11-03-25 AM.png[/attachment]
Thanks a lot for your help! That was very helpful.