I have an OPC heartbeta tag that I want to monitor, and display status OK or NOT OK accordingly, based on whether I receive true from the tag after 30 seconds or not. Is there a way to monitor the tag value and using some time function add a script binding with mapping?
Example case:
if (time after 30 secs):
if (heartbeat) == true:
text = OK
else:
text = False
Please see Wiki - how to post code on this forum.
Create an expression tag to monitor the heartbeta(!) tag.
{[~]heartbeat}
(now() - {[~]heartbeat.Timestamp} > 30000)
I would monitor the tag's timestamp for being within the last 30 seconds.
Yes, but is there a function for getting the timestamp? .Timestamp doesnt seem to be working. Do i also enable history on the heartbeat signal?
Did you try what I suggested? It will return true if the timestamp is older than 30,000 ms (30 s).
That's what you asked for, but I don't think that's what you want.
@sfatimazahrak what is your current objective? Try explaining it so we can try to help you
I did, but the timestamp being returned is way larger, which is why Im confused. What im trying to do is monitor the value of the tag (RM_VLD_LLM), its a heartbeat signal sending a 1 after every 30 secs. I want to use that to display the status of the signal as text, i.e if heartbeat gives me 1 after 30 secs I want to display OK, otherwise i want to display FAULT. The condition needs to monitor the tag for every 30 secs, I have enabled history on the tag and given it a sampling rate of 30 secs.
Essentially, every 30 secs I wanna check for a heartbeat and display the status accordingly.
I did, but the timestamp being returned is way larger, which is why I'm confused.
A tag timestamp is the number of milliseconds since 1970-01-01 00:00:00, the dawn of Unix time. The timestamp for today will be a large number.
What you should be doing is sending an alternating 0 - 1 - 0 - 1 ... signal, changing every 30 s.
No, what you want is that if the tag timestamp is less than 30 s old you want the monitor tag to go true, else false.
No, it needs to monitor continuously - probably at the default rate of 1000 ms.
History is for recording history. You're not interested in history. You're interested in now. Disable the history.
Create an expression tag, say heartbeatGood, to monitor the heartbeat tag.
Set the expression to,
(now() - {[~]heartbeat.Timestamp}) < 30000
This tag will now turn true if the last heartbeat change was within the last 30 s and false if it doesn't change for more than 30 s.
On the label component text property create an expression binding:
if({[~]heartbeatGood, 'OK', 'FAULT')
Is this tag coming from an external OPC server, like one built-in to a PLC? If so, that device's clock is the source of the timestamp, and if wrong, it will be broken.
The number is elapsed time in milliseconds. Between your two screenshots there is 1hour 19min and 7 sec difference between the timestamps. That's 4,747,000 total milliseconds, which is close to what you got by a couple of minutes. Just take the result and divide by 1000 if you want it in seconds.