Help With A-B Connection Path

Trying to setup connection path to a DH+ based SLC 5/04 Processor At Node 6 by going through a ControlLogix at 192.53.3.30 using 1756-DHRIO/D Channel B in slot 9

Selecting A-B SLC Driver and current path that is not working is

192.53.3.30,1,9,3,6

I tried setting up just a connection to ControlLogix processor at 192.53.3.30 only and it works fine. We can see the SLC from RS-LINX at the facility.

Ignition7.9.12

Thanks In Advance

Remove 192.53.3.30 from the connection path, just use it as the hostname. The connection path would then be 1,9,3,6. If your connection path ever has an odd number of components you’ve built it incorrectly.

You again are the man Kevin ! Be glad when this DH+ stuff is gone …