How do I connect a Schneider M340 PLC to Ignition?

I already added and IP address to the PLC and I am able to ping it

Most often people use the Modbus driver to connect to the M340.

You'll need to know the relevant Modbus addresses to get anything useful out of it.

I have successfully moved Booleans and Integers by following the Ignition Manual directions. Being that said I have not been able to move Float. I am using a REAL variable in M340, HRF and Float in Ignition. Any Suggestions?

Try the "Reverse Word Order" setting on the driver.

1 Like

It worked. Thanks Kevin