I'm configuring an OPC Tag in Ignition to read a value from a Siemens S7-300 PLC.
The PLC address I was given is:
DB916,DBD228
The OPC device name in Ignition is:
L12_VarioAsep
The OPC Item Path is currently configured as:
ns=1;s=[L12_VarioAsep]DB916,REAL228
The tag quality is Good (no errors or Bad quality), so the communication appears to be working. However, the tag value is always 0, even though I expect it to contain a non-zero value.
My questions are:
- Is this the correct OPC Item Path for the PLC address
DB916,DBD228? - Should
DBD228be read asREAL228,DINT228, or another data type?
Unfortunately, I don't have access to the PLC project or STEP 7/TIA Portal.
Any suggestions or troubleshooting steps would be greatly appreciated. Thank you!