How should I read S7-300 DB addresses (e.g. DB916,DBD228) in Ignition OPC?
I'm configuring an OPC Tag in Ignition to read a value from a Siemens S7-300 PLC.
The PLC address I was given is:
DB916,DBD228
The OPC device name in Ignition is:
L12_VarioAsep
The OPC Item Path is currently configured as:
ns=1;s=[L12_VarioAsep]DB916,REAL228
The tag quality is Good (no errors or Bad quality), so the communication appears to be working. However, the tag value is always 0, even though I expect it to contain a non-zero value.
My questions are:
  • Is this the correct OPC Item Path for the PLC address DB916,DBD228?
  • Should DBD228 be read as REAL228, DINT228, or another data type?
Unfortunately, I don't have access to the PLC project or STEP 7/TIA Portal.
Any suggestions or troubleshooting steps would be greatly appreciated. Thank you!
The D is probably DWord, so I'd expect it to look like [Device]DB916,D228 in Ignition
If you just use [L12_VarioAsep]DB916,REAL228 for the path and Float for the data type, do you get values?