How to connect Rockwell compact logic to ignition system

Yes, Ignition's OPC server will allow you to browse the tags in your PLC.

I'm not sure what question you're asking here. The PLC will need programming in order to perform it's intended function. There is no additional configuration, aside from general communications, needed for Igntion to connect to the PLC.

Ignition comes with a OPC-UA server. The AB Device Driver, allows for OPC subscriptions to be made to the PLC. However, there are some caveats to the best way to configure Ignition to work with AB devices.

Also, avoid adding tags to ignition that you don't need in Ignition. Don't just drag the entire Controller folder into ignition.

Here are some good topics that are of relevance.