How to find registers at Huawei smart logger 2000

Hello!
I am new to ignition.
HUAWEI SMART LOGGER 2000 is connected to Ignition 7.5.2 by the Modbus tcp protocol. How can I find the addresses of the registers on which the data is displayed to create tags? There are no registers in the manual for this device.

Thanks,Oleh

Hi Oleh and welcome to Ignition!

Modbus is a funny beast - have you tried searching for registers using Chipkin Modbus Scanner or something similar? It’s a free download and has helped me out a few times.

I have not used any search tools yet. I did not know where to start. I’ll try chipkin modbus scanner.
Thanks)