I have ignition perspective project running in the main PC.
now I want to run same project on other pc/laptop.
I have tried adding outgoing connection but it says it is faulted.
I can ping all of the remote devices but I can not add into connections. I have local gateway as 192.168.1.xxx/8088 and one of the remote gateway is 192.168.1.xxx/8089.
( I am not using SSL connection)
Do you want to run a client connected to the original gateway? Or are you trying to duplicate the gateway into another? Please explain the architecture you are trying to achieve.
You have independent gateways, based on your request. They don't sync.
If you want a single application for the site that all clients use, you would use a single gateway. Point just the browsers (or Perspective Workstation) on the other client machines at the one gateway. The one gateway would make all device and database connections.
If you really do need separate gateways (for whatever reason), and you want to share projects, you will need to use the Enterprise Administration module to move resources around.