We have two PLCs, and we would like to display a separate Alarm Status Table for each PLC.
Right now, the Alarm Table shows alarms from both PLCs together.
What is the best way to filter the Alarm Status Table so each PLC only shows its own alarms?
On the alarm status table, there's a Filters.Conditions property. Source/DisplayPath/Provider are all possible. Assuming you have a common part of your tagpath that you can filter against..
Are your tags for the different PLCs in different folders? Put the folder name in the source path. If they're all mixed together then that's a harder problem.