Ignition Alarms 8.0 False Positive?

Can anyone tell me why this alarm is being triggered? I have a SQL tag that grabs the last temp value of a data logger. The sensor has always been between the set points of 64.4 - 82.4, but is showing up in the alarm log. Also the notification for this alarm is not being sent from SMTP. When I have another alarm for testing triggered with the same alarm pipeline, the email is sending correctly.


image
image

Hi Mason,

Is it possible that the Event Value has reached either setpoint, as you’ve got Low inclusive and High Inclusive set to “true”.

Is “Active Pipeline” configured in the alarm notification similar to the other alarms that are sending out emails?

Regards,

Ali