Ignition Communication with Eurotherm EPack

I have a customer that is interested in communicating with their Eurotherm EPack temperature controllers without a PLC (Ignition to EPack over Ethernet/IP). Does anybody have experience with the eurotherm Epack and communications with it.

Not with that specifically, but I have substantial experience with EtherNet/IP, and a module that implements most of its feature set:

Automation Professionals' EtherNet/IP Suite

More details here:

Do you have the EDS file and/or links to the user manual?

EPack_V603.eds.zip (2.8 KB)

Here is the eds file

Looks pretty simple for scanner mode. You presumably configure the order of input and output registers (up to 32 and 16, respectively) in the Eurotherm device itself.