Ignition edge OPC - UA faulted
I have configured OPC-UA by using Ignition edge. I am getting tags from Codesys (OPTO 22 Controller) Groov Epic PR1. After sometime OPC-UA server is going to faulted automatically and it is not re-connecting again. I have tried maximum ways for fix this issue, but i can’t able to fix this…
Please let me if have any solution for this…!!
Check the logs (post here, using pre-formatted option).
I will boot one of my Groovs’ later and try and help more.
Go to status/logs and type “OPC” into the filter.
Copy and paste the text here using the preformatted button (it looks like this </>) in the menu above where you type.
And welcome to the community!
Also, is this a one box solution?
Groov is running Edge within the PAC?
Not PAC, Groov is running in CODESYS Controller
Groov (EPIC) is a product name, a description of a hardware Programmable Automation Controller. PAC Control is an IDE that uses OptoScript.
Where is Edge running, internally on the Groov hardware or on a separate IPC?
Edge is running on the groov hardware
Just now again Ignition edge gone to fault mode, This is latest Log file while get faulted
UascClientMessageHandler	07Feb2021 17:25:20	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 17:25:04	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 17:24:48	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 17:24:40	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 17:24:36	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
SessionFsm	07Feb2021 17:24:03	[8] Keep Alive failureCount=2 exceeds failuresAllowed=1
UascClientMessageHandler	07Feb2021 16:04:35	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:04:19	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:04:03	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:03:47	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:03:31	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:03:15	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:02:59	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:02:43	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:02:27	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:02:11	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:01:55	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:01:39	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:01:23	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:01:07	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:00:51	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:00:35	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:00:19	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:00:03	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:59:47	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:59:31	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:59:15	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:58:59	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:58:43	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:58:26	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:58:10	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:57:54	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:57:38	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:57:22	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:57:06	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:56:50	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:56:34	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:56:18	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:56:02	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:55:46	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:55:30	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:55:14	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:54:58	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:54:42	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:54:26	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:54:10	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:53:54	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:53:38	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:53:22	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:53:06	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:52:50	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:52:34	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:52:18	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:52:02	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:51:46	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:51:30	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:51:14	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:50:58	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:50:42	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:50:26	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:50:10	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:49:54	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:49:38	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:49:22	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:49:06	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:48:50	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:48:34	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:48:18	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:48:02	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:47:46	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:47:30	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:47:14	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:46:57	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:46:41	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:46:25	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:46:09	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:45:53	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:45:37	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:45:21	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:45:05	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:44:49	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:44:33
Did you follow Opto University for setup?
I’ll be honest, I don’t use CoDeSys version.
You might get a faster reply here: https://forums.opto22.com/
Or maybe @Kevin.Herron can advise what logs to change to trace to narrow it down.
This is a bug in codesys servers that we’ve implemented a workaround for in 8.1.1 or 8.1.2.
Thank you…!!
Is there any alternative solution?
Upgrade to a version of codesys that fixes it, if there is one.
Or change to PAC control within the EPIC.
Ok…
I checked release notes, it should be fixed in 8.1.1 or later:
Implemented workaround for reconnecting to servers that don't respond correctly to subscription transfer requests.