Ignition Edge to Standard: Historical Tags Not Working

I have two Ignition applications: one is the Standard version, and the other is the Edge version. In my Standard application, I have a configured database. I want the tags from my Edge application to be stored in the database of my Standard application, which has the Tag Historian module.

I configured the Gateway Network by creating an outgoing connection from Ignition Edge to Ignition Standard and set up the DataSync in the Edge application. However, when I insert a Power Chart into the view, I don't have access to the tags configured with history.

Datasync config:
Remote Gateway Name: (gateway IP adress)
Remote History Provider Name: History Tags Provider name from
Standard application.
Remote History Sync Enabled: Enabled

Datasync Overview:
Only one row: Name, Sync Type, Current Sync ID
Edge Historian, Tag Historian, 0

Can anyone help?

Use the gateway name, not the ip address, in the remote sync setup.