I used TIA V.18 from Siemens With Simatic S7-1500 as PLC. For HMI , I used Ignition Platform V 8.1.18. I used OPC-UA for communication between S7-1500 and Ignition.
The problem I have is the numbers flash to zeros, even though the values from PLC did not change. I used trap to test this.
Please add the vision or perspective tag to your question. The answer may depend on which you are using.
What sort of trap? Did you monitor these on Designer's Tag Browser?
Is there any error overlay on the Ignition Vision or Perspective HMI?
lrose
April 15, 2024, 3:16pm
3
When do they flash to zero? In some circumstances this is expected behavior.
It is random and I can not predict. Sometimes only 1 flashes and sometimes all of them flash.
lrose
April 15, 2024, 3:29pm
5
Does this happen when you first open the window, or while the window has already been open?
it happens when the window has already been open
You should share how your tags are configured.
We are still waiting for this. It looks like Vision.
Please let me know how can I show that
Click the pencil icon beside your question title. There are dropdowns for the tags.
