On what port and what driver do we connect a RedLion to Ignition OPC UA???
Port 790???
Modbus??
Thanks
On what port and what driver do we connect a RedLion to Ignition OPC UA???
Port 790???
Modbus??
Thanks
If the device supports Modbus then use that driver. The port used by Modbus is 502. We would need more specific information about the PLC to answer this question.
Thanks Greg for yoru reply
ProducTVity Station
redlion.net/Products/Groups/ … /07051.pdf
It has a built in OPC Master, but can not connect to it
And also pull data from a RedLion G306
redlion.net/Products/HumanMa … /G306.html
Thanks for your suport
you need to use the opc-da module, not opc-ua.
Using OPC-DA you may want to take a look at this article
Thanks Greg for your information. Will follow up on your recommendations
Cheers