Ignition SCADA perspective compile error (Motor circuit)
'm trying to get a script running when i pressed the button on my circuit which runs a motor, the script is tied to onActionPerformed event, but when I run it, it gives me this error. The tags are correct and inserted in the script correctly.
"Unable to run action 'component.onActionPerformed' on MotorControl@D/root/Button: code could not be compiled."
The code for this event is:
def runAction(self, event):
    # Define the tag paths for motor control and motor running time
    motorStatusTagPath = "[default]My_Tags/Motor_Status"
    # Motor control tag (on/off)
    runningTimeTagPath = "[default]My_Tags/Motor_RunningTime"
    # Motor running time tag
    # Read the current motor status (True = running, False = stopped)
    currentMotorState = system.tag.readBlocking([motorStatusTagPath])[0].value
    # Read the current motor running time
    currentRunningTime = system.tag.readBlocking([runningTimeTagPath])[0].value
    # Toggle the motor state (on/off)
    system.tag.writeBlocking([motorStatusTagPath], [not currentMotorState])
    # If the motor is running, increment the running time by 1 (you can adjust the increment value
    as needed)
    if not currentMotorState:
    # If the motor is turned on
    system.tag.writeBlocking([runningTimeTagPath], [currentRunningTime + 1])
    # Increase running time
  1. Check the third comment line from end doesn't have a line break in front of "as needed)".
  2. Your last line of code should be indented for the if logic.
org.python.core.PySyntaxError
  File "<function:runAction>", line 2
    testTagPath = "[default]My_Tags/Motor_Status"
SyntaxError: mismatched input 'testTagPath' expecting INDENT
	at org.python.core.ParserFacade.fixParseError(ParserFacade.java:95)
	at org.python.core.ParserFacade.parse(ParserFacade.java:205)
	at org.python.core.Py.compile_flags(Py.java:2269)
	at com.inductiveautomation.ignition.common.script.ScriptManager.compileFunction(ScriptManager.java:899)
	at com.inductiveautomation.ignition.gateway.project.ProjectScriptLifecycle$TrackingProjectScriptManager.compileFunctionSuper(ProjectScriptLifecycle.java:825)
	at com.inductiveautomation.ignition.gateway.project.ProjectScriptLifecycle$AutoRecompilingScriptFunction.getOrCreateDelegate(ProjectScriptLifecycle.java:941)
	at com.inductiveautomation.ignition.gateway.project.ProjectScriptLifecycle$AutoRecompilingScriptFunction.<init>(ProjectScriptLifecycle.java:932)
	at com.inductiveautomation.ignition.gateway.project.ProjectScriptLifecycle$TrackingProjectScriptManager.compileFunction(ProjectScriptLifecycle.java:805)
	at com.inductiveautomation.ignition.common.script.ScriptManager.compileFunction(ScriptManager.java:882)
	at com.inductiveautomation.perspective.gateway.script.ScriptFunctionHelper.lambda$invoke$0(ScriptFunctionHelper.java:115)
	at java.base/java.util.concurrent.atomic.AtomicReference.updateAndGet(Unknown Source)
	at com.inductiveautomation.perspective.gateway.script.ScriptFunctionHelper.invoke(ScriptFunctionHelper.java:108)
	at com.inductiveautomation.perspective.gateway.script.ScriptFunctionHelper.invoke(ScriptFunctionHelper.java:98)
	at com.inductiveautomation.perspective.gateway.action.ScriptAction.runAction(ScriptAction.java:80)
	at com.inductiveautomation.perspective.gateway.model.ActionCollection$ActionSequence$ExecuteActionsTask.lambda$call$0(ActionCollection.java:263)
	at com.inductiveautomation.perspective.gateway.api.LoggingContext.mdc(LoggingContext.java:54)
	at com.inductiveautomation.perspective.gateway.model.ActionCollection$ActionSequence$ExecuteActionsTask.call(ActionCollection.java:252)
	at com.inductiveautomation.perspective.gateway.model.ActionCollection$ActionSequence$ExecuteActionsTask.call(ActionCollection.java:221)
	at com.inductiveautomation.perspective.gateway.threading.BlockingTaskQueue$TaskWrapper.run(BlockingTaskQueue.java:154)
	at com.inductiveautomation.perspective.gateway.threading.BlockingWork$BlockingWorkRunnable.run(BlockingWork.java:58)
Ignition v8.1.47 (b2025022612)
Java: Azul Systems, Inc. 17.0.13
Your code line 2 says,
Your error indicates that line 2 is,
Which is it?
The error message indicates that you're missing an indent. This could mean that you've used a tab in some places and 4 × space characters in others.
My code definitely says motorStatusTagPath
I've tried fixing the indents not mixing them with spaces but still won't run
Look for a second event on the button. I suspect that you'll find one with the testTagPath line in it.
Ok that's removed (just added that to test the button) but the new error is:
com.inductiveautomation.ignition.common.script.JythonExecException
  File "<function:runAction>", line 19, in runAction
TypeError: unsupported operand type(s) for +: 'NoneType' and 'int'
	at org.python.core.Py.TypeError(Py.java:234)
	at org.python.core.PyObject._basic_add(PyObject.java:2091)
	at org.python.core.PyObject._add(PyObject.java:2068)
	at org.python.pycode._pyx7.runAction$1(<function:runAction>:19)
	at org.python.pycode._pyx7.call_function(<function:runAction>)
	at org.python.core.PyTableCode.call(PyTableCode.java:173)
	at org.python.core.PyBaseCode.call(PyBaseCode.java:306)
	at org.python.core.PyFunction.function___call__(PyFunction.java:474)
	at org.python.core.PyFunction.__call__(PyFunction.java:469)
	at org.python.core.PyFunction.__call__(PyFunction.java:464)
	at com.inductiveautomation.ignition.common.script.ScriptManager.runFunction(ScriptManager.java:847)
	at com.inductiveautomation.ignition.common.script.ScriptManager.runFunction(ScriptManager.java:829)
	at com.inductiveautomation.ignition.gateway.project.ProjectScriptLifecycle$TrackingProjectScriptManager.runFunction(ProjectScriptLifecycle.java:868)
	at com.inductiveautomation.ignition.common.script.ScriptManager$ScriptFunctionImpl.invoke(ScriptManager.java:1010)
	at com.inductiveautomation.ignition.gateway.project.ProjectScriptLifecycle$AutoRecompilingScriptFunction.invoke(ProjectScriptLifecycle.java:950)
	at com.inductiveautomation.perspective.gateway.script.ScriptFunctionHelper.invoke(ScriptFunctionHelper.java:161)
Caused by: org.python.core.PyException
	... 29 more
You'll need to repost the current code (with the comment and indent corrected) and tell us which is line 19. (In the original post line 19 is a comment.)
I've removed line 19 which was a comment but still same error
Highly likely that your timestamp tag either is null or you are reading the wrong path.
system.tag.writeBlocking([runningTimeTagPath], [currentRunningTime + 1]) is likely the line that is causing the error but the true cause is that for some reason your currentRunningTime value is null instead of a number.
Post your modified code so we can confirm/review for other issues.
Ok I changed the tag Motor_RunningTime from null to 0, now every time I press it increments, no error.