Ignition SCADA Server Sizing for ~100,000 OPC UA Tags

Hi All,

We are evaluating Ignition SCADA for an industrial automation application where approximately 100,000 OPC UA tags will be integrated from the control system.

I would like to understand the recommended Ignition Gateway/server sizing for this scale.

Could you please share your experience or recommendations regarding:

  • Recommended CPU/core count
  • Recommended RAM
  • Storage requirements
  • Practical tag capacity per Gateway
  • Impact of different OPC UA scan rates
  • Impact of alarming and tag historian
  • Perspective client load
  • Whether a single Ignition Gateway is suitable for ~100,000 tags or whether a distributed architecture is recommended
  • Any benchmark or reference architecture available for similar-scale systems

The intention is to understand the infrastructure required before proceeding with performance validation.

I've got a client running a standard redundancy setup with around 150k tags between the 2 main PLCs with another 60 or so other devices reading about a dozen tags from each. The other devices are modbus and ABB TotalFlow devices. The main PLCs were ControlLogix L83 processors in the past but new plants are now the L908TS models. We're using our own AOIs and UDTs for these projects and have optimized the comms to reduce load on the processors. They're running 8 core VMs with 16GB of RAM on Windows Server 2025. I believe the host is using Xeon Gold processors but it's have to check. I've configured Ignition to use a maximum memory of 8GB and CPU usage sits around 5% with some spikes up to 10% here and there. We have anywhere from 4-6 Vision clients running at a time with occasional increases here and there depending on anyone remoting into the system.

We have a separate server running Postgres with TimescaleDB for the historian and other databases (audit log and alarm journal). We're historizing about 7,500 tags and store around 15M values per day. Performance of the historian has been great also.

Thanks for the details Michael. Just to clarify your architecture, with the standard redundancy setup, are you running two Ignition Gateway VMs (Primary and Backup), each with 8 cores and 16 GB RAM, plus a separate PostgreSQL/TimescaleDB server? Also, are the 4–6 Vision clients running on separate client machines/VMs, or are they only concurrent Vision client sessions?

Primary and backup are on separate hosts. Since Ignition doesn't do load balancing between redundant gateways, all clients are running off of the active server (typically the master).

2 clients are 2 redundant servers running ThinManager with thin clients running load balanced (1 per server but fail over to the other server if one RDS server goes down). These 2 clients are running 4K TVs with a quad window setup so they can have 4 windows pulled up at once (still a single client though). The other 2 clients are panel PCs in the plant.

The other variable clients beyond the 4 are myself when doing development and testing and other users on a separate RDS server where we allow any number of clients to connect. Usually during a startup we have 3 or 4 engineers or more monitoring the system from their laptops on this remote connection on a single client RDS server.

Once normal operations is in place the remote connection won't be used as heavily but still gets used daily.

Welcome to the forum!

Some additional information that should be useful and covers this topic.

One point to consider is what sort of scan rate are you expecting on average? A remote monitoring system with 30-60 sec poll times vs a local server acting as a plant HMI and 1 second poll times is a significant difference in compute power.

But generally speaking Ignition is relatively lightweight. We have 40k OPC tags so far and it's a rounding error in terms CPU usage.

Hi Sfenwic,

We are planning an Ignition architecture for approximately 150,000 OPC UA tags with the following assumptions:

  • Polling interval: 1 second
  • Expected tag changes: 50%, approximately 75,000 value changes/sec
  • Back-End Gateway: 1 VM, 16 vCPU / 32 GB RAM
  • Front-End Gateway: 1 VM, 8 vCPU / 16 GB RAM as a planning assumption
  • Historian / SQL Database: 1 separate VM
  • Concurrent clients: approximately 50
  • Redundancy: Not currently planned
  • Total preliminary architecture: 3 VMs

Based on the benchmark sizing, 150K tags can be accommodated by one active back-end gateway, but there is effectively no tag-capacity headroom, and the expected value-change rate is relatively high.

Could you please review and confirm whether this architecture and resource sizing are appropriate for the above workload, particularly the 75,000 changes/sec historian workload, or whether you recommend a scale-out architecture?

Inductive has a sales team that you can engage with, you'll probably find it more meaningful to reach out to them and go through your architecture plans rather than the forum.

IA's server sizing guide is pretty loose because Ignition workloads are very sensitive to integrator/end user competence. The guide says to test your workload.

Spend some money setting your application up on rented servers and test it. Asking for more precision from anyone is not possible without this step.

Workloads are also very sensitive to the device sourcing the data, and the complexity of the network path that delivers the data.

10 PLCs on a local factory network will deliver 100k tags much more efficiently than 1000 low quality modbus devices delivering 100 tags each.

There are many factors outside of Ignition that need to be accounted for.