Ignition server need to be a server?
Does the Ignition server need not be a true server? Would a Dell Precision with 8GB of memory work as well?
It will be storing the MySQL data and the Ignition database/configuration.
I will be monitoring and controlling 10 pieces of equipment at around 30 analog points and 500 digital tags for each piece of equipment.
I’ve run Ignition on a Dell OptiPlex on previous jobs that didn’t require much in the way of redundancy. Worked just fine. One project was monitoring around 200 analogs and 350 discretes, with quite a bit of timed scripting in the background.
Ignition can run on many kinds of computers. From low-end whimpy spec computers to high-end powerful computers. It depends on what you want to do with Ignition.
Specifically to your question, I have been using a Dell Precision T3500 (8Gb memory) as an Ignition Gateway with MySQL on Ubuntu 12.04 for 9 months or so. This one has about 4000 tags to 3 controllers (ControlLogix, CompactLogix and Modicon), database connections to both the local MySQL and corporate MSSQL databases, and typically 6 clients. It’s running about 2-3% CPU utilization for Ignition, so I think it’s safe to say that it could do a lot more…
What would be a recommendation for a computer that will sit inside an electrical panel? It’s purpose will be to serve as a gateway for about 100 plcs and 50,000 tags?
The key to use in an electrical panel is usually temperature tolerance. Plus adequate cooling to dissipate the heat produced by high-performance CPUs, to keep the panel interior under the limit.
Not so simple for the heavy load you suggest.
Yep, the OnLogic fanless models only go to quad-core, you’d definitely need your DB on a separate server for 50K tags.
This could be an option if your enclosure was large enough;
Bought a couple of these Helix 500 Fanless Intel i9 10-core models from Onlogic recently. Have not (and won’t get to) try them on 50,000 tags and 100 PLC’s however.
Onlogic Helix PC’s