Ignition to OPC Router Connection Error

Hi!
I try to connect Ignition Vision 8.43 to OPC Router. Previously I have connected Kepserver EX to OPC Router without any issue. I got error


Ignition-MESBootCamp_Ignition_logs_20241125-2001.zip (2.3 MB)

From OPC Router side, I get the error below:


Any idea?

In the top screenshot you are making an OPC UA connection from Ignition, to OPC router, where Ignition is the client.

In the bottom screenshot it appears you have reversed the roles and are trying to connect OPC Router as the client to Ignition's OPC UA server, using the wrong endpoint information.

What are you actually trying to accomplish?

Hi, Kevin,
right, OPC Router must be Client.

Ignition's discovery endpoint if you haven't changed any settings will be opc.tcp://localhost:62541/discovery. OPC Router must be on the same server in this case.

If you need to access it from another machine you have to change the Bind Address to something like 0.0.0.0 and then restart the gateway.

1 Like