We have been having issues where tag values from our RTU drop to 0 at random intervals. Certain tags drop at the same time, and it is for a split second. We have engaged Inductive Automation on this and troubleshooting, but since it seems like a complex issue, I am reaching out to the wider community to see if anyone has come across this before.
The drops are very quick and basically a flicker on the screen, but trends reveal the drops:
We have:
- about 400 tags
- monitored with Wireshark and can see the packet come with a 0 value
- set poll rates to 5s
- two servers both with a connection to an RTUs and behaviour is seen on both sets,
- split tag groups for analogs, binaries, inputs and outputs one one server - still have the behaviour.
- performed firmware updates on RTU
- tried to use class based polling with AnalogInputx BinaryInputx addressing but the OPC UA Server does not list all the data points and ‘loses’ some points at times - this was done with the idea to rule out the possibility that gvi address mismatches could cause weird behaviour
- tried using gvi addressing but problem persists
- tried disabling most tags and monitoring for ‘drops’ and still got drops even with 4 tags enabled
- also disabled class based polling while using gvi addressing, slowed down heartbeat tag frequency to every 4s
Planning to try next:
- Try connecting to RTU on site eliminating as much of the network as possible
- Try old DNP3 driver and observe
- Connect to RTU via Kepware and observe
- Disabling all but one tag and observe and add tags gradually again to see if a specific tag causes this
Hoping someone has seen this before and can provide other suggestions.