Ignition UA connectivity between VM's
Dear Folks,
I have a requirement to test OPC-UA connectivity between 2 VM’s created using virtualBox. I have done the following
  1. Created 2 VM’s with windows 8.1 64bit OS
  2. Created NAT network between VM’s
  3. I have tested network connectivity between VM’s by pinging the respective IP address and I got response.
  4. In one of the VM I tried to configure OPC-UA client to connect to other VM’s OPC-UA server. I configured following Endpoint URL: opc.tcp://192.168.10.5:62541/discovery.
I got following error message:
When using 62541 port I have this error: UaException:status=Bad_Timeout,message=io.netty.channel.connectTimeoutException: Connection timed out:/192.168.10.5:62541
When using 8088 port I have this error:
UaException:status=Bad_Timeout,message=timed out waiting for acknowledge
I have tried other ports like 8088/4096
Is it a network issue or something else?
Thanks & Regards,
Saravanan.
Tried temp disabling firewalls?
I haven’t used virtualbox in quite a while, but I recall that the default NAT network type restricted VM-to-VM communications.
Ignition’s OPC UA server binds to localhost by default. Did you change the bind address on the gateway that will receive the connection to 0.0.0.0 and restart?
I have tried but of no use still in trouble.
But I am able to ping the VM’s
Hi Kevin,
Thankyou for the answer, should I change the binding IP address on OPC-UA server side? Which Address I shall put there?
Yes, on the gateway that will receive the connection under Config > OPC UA > Server Settings set the Bind Address to 0.0.0.0 and restart.
Thanks a lot Kevin, It worked… :slightly_smiling_face: