Ignition with Schneider OFS OPC UA Setup Help

Has anyone used ignition with Schneider OFS OPC UA? I’m have trouble connecting the two.

Any suggestions would be greatly appreciated. Thank you.

What’s the error you’re getting?

Typically one of the first problems people run into when connecting to 3rd party OPC-UA servers is that you need to figure out where in the server you can install or verify that Ignition’s UA client certificate is trusted.

[quote=“Kevin.Herron”]What’s the error you’re getting?

Typically one of the first problems people run into when connecting to 3rd party OPC-UA servers is that you need to figure out where in the server you can install or verify that Ignition’s UA client certificate is trusted.[/quote]

Thank you very much! It is indeed that the certification caused the issue.

Hi, I can see that I’m bumping an old thread here but are you able to describe the steps you took to certify the Ignition client in OFS?
My client can definitely see my UA server and there’s no obvious place in OFS where you just import a certificate or CSR to make it work.