Hi everybody,
I have to connect a ControlLogix Revision 32 with the ignition V7.9.10, i used the OPC UA server in the gateway page. My problem, I configured all the features in the page, and at moment when i go to the ignition designer, i cannot see the tags, i tried to see the tags in the page with the quick client, and dont appear the global tags from the PLC. If someone have the samme problem or similar, i would like to know how to see the tags to drag to the ignition designer.

Looks like you set up the device connection with the legacy driver instead of the one that is for v21+ firmware revisions.
As @Kevin.Herron notes, are you using this driver?