We are trying to set the date and time to a device over Modbus. The spec for the device seems easy, just not sure if ignition has the math to do it. You just set a few registers, but here is the problem. On a single register we need to set the first 8 bits to the day and the second 8 bits to the month. Is there a way to do this in ignition?
Thanks
Luke
bits 15 to 8 = month (1 to 12) P3: bits 7 to 0 = day (1 to 31)
How about something like this:
month = 1
day = 30
dataReg = (month<<8)+day
system.tag.write("YourTagPath",dataReg)
You may need to flip the order around - Modbus is supposed to be big-endian, but word order differs between different devices.
today = system.date.now()
day = system.date.getDayOfMonth(today)
month = system.date.getMonth(today) + 1
word = (month<<8) | day
system.tag.write("SomeTag", word)
Thanks, This will get us well on our way.