Is it possible to dynamically update column names using a Transaction Group?
Hi everyone,
I have a question regarding Transaction Groups in Ignition.
Currently, I’m using a Tag Change Script to update torque and angle values in different columns of a database table, depending on a Counter value read from the PLC. The column names are built dynamically, like Torque1_NM, Torque1_Angle, Torque2_NM,Torque2_Angle, Torque3_NM,Torque3_Angle, etc., depending on the current step.
Here’s a simplified version of what I’m doing:
def update_data():
   from time import sleep
   sleep(0.15)
   VIN = system.tag.readBlocking(["[Amvian]_PLC_/Controller:Global/Traceability_ST1/VIN_Number"])[0].value
   Counter = system.tag.readBlocking(["[Amvian]_PLC_/Controller:Global/Traceability_ST1/Torque_Counter"])[0].value
   T_NM = (system.tag.readBlocking(["[Amvian]_PLC_/Program:STATION1/Torque/AtlasCop_ST1_High/TorqueValue"])[0].value)/100
   T_Angle = system.tag.readBlocking(["[Amvian]_PLC_/Program:STATION1/Torque/AtlasCop_ST1_high/Angle"])[0].value
   try:
   	query = "UPDATE `amvian_db`.`data` SET `Torque{}_NM`=?, `Torque{}_Angle`=? WHERE  `VIN`=?;".format(Counter, Counter)
   	args = [T_NM, T_Angle, VIN]
   	system.db.runPrepUpdate(query, args)
   	print(query)
   	print(args)
   except:
   	print("Error al actualizar dato: {}".format(VIN))
   system.tag.write("[Amvian]_PLC_/Controller:Global/Traceability_ST1/Update_DATA",0)
My question is:
Can something like this be replicated using a Transaction Group?
Specifically, is there a way to dynamically define which columns are updated in the database, based on a tag value like Counter, within a Transaction Group?
Or more generally, do Transaction Groups allow any kind of dynamic logic to define column names at runtime?
Thanks in advance for any guidance or suggestions!
I'm not aware of a way to dynamically set the column names within a transaction group but if I had to solve this problem I would do it with several transaction groups, one for each step, all targeting the same table but triggered on a different value (i.e. counter=3 for step 3).
A couple of things to note about the script that you posted.
  1. The use of sleep() is generally a bad practice and searching in these forums will tell you many reasons why.
  2. Whenever reading or writing tags, consolidate all tags to be read or write into a single system.tag.readBlocking or writeBlocking function call for better performance.
The short answer to this question is no.
The longer answer is still no, but also: Why do you want a transaction group if you've got a functional script?
Separately:
This is (probably) a sign of bad database design. If you have any control over the process at all, I would recommend reconsidering this decision. Dynamic column names are a smell - relational databases are much happier over time with properly normalized data. In other words, based on your (very small) sample you should have three columns: Sensor (or whatever identifier), NM, and Angle, and always add rows to those three columns.
The reason I'm exploring Transaction Groups is mainly because I need reliable feedback/handshaking. In the Transaction Group I’ve used before, I can easily configure a handshake tag to confirm that the operation completed. That feedback loop has been very useful.
With the script, the only feedback I’ve set up is writing a tag to 0 at the end (to use a falling edge as a trigger). But that tag never seems to go back to 0, even though:
  • The script runs correctly.
  • The tag path is valid.
  • Nothing else is forcing that tag back to 1 (I’ve checked).
So I’m unsure if:
  1. The script finishes before the write happens.
  2. There's a threading/timing issue.
  3. Something else is overwriting the tag without me knowing.
That’s why I thought maybe a Transaction Group would be more robust for handling the handshake/feedback mechanism, even if it’s more rigid in logic.
Any suggestions on how to improve feedback reliability in this case (with scripting or otherwise) would be appreciated.
A script allows you to capture both the fact that execution failed (via an exception) and why it occurred, which is strictly more information than is available in a transaction group handshake.
I would not pursue transaction groups for this purpose.
Try adding catch blocks that explicitly capture both Java and Python exceptions:
Ok. I will try that. Thank!