Good morning.
In Ignition 8.1.15, I have noticed that it is not possible to reference a Tag in the Alarm.Label property for a UDT. If a Tag is referenced, the Label value is null.
Instead, with “DisplayPath” it works correctly.
Definition of the Alarm in the UDT:
Alarm on an instance of the UDT:
Best Regards.
Don’t they need curly braces around the tag paths?
I’m on 8.1.19 and do not see an issue. To test, use an expression with static text, like ‘test’.
@nminchin There’s no need. It’s a tag, not an expression. Notice that “DisplayPath” works correctly.
I just tested with [System]Gateway/SystemName and label will remain null until the alarm is first triggered. Tested on 8.1.19.
Exact. It’s strange because DisplayPath does show value from the beginning.