Keyence KV-NC32T on Ignition using Mitsubishi Driver

Hello, i read a few days ago that there is a way to connect a PLC KV using the driver Mitsubishi TCP Q series, I read the conversion table below, the status for the PLC on ignition is "Connected", but, when I try to read the tags on QuickClient, the connection of those tags are "Bad", I don't know if it is a mapping issue, or if there is something else that i forgot to configure, can you help me please?

And this is the mapping that i'm using:

Does this mean you've configured an address mapping on the gateway for this device? What does that look like?

Can you get a Wireshark capture of the read attempt?

I think i made it wrong, i thought that i only had to do the convertion on ignition, but, I also have to activate the MC protocol on the PLC right? and do the mapping from the PLC, then i'll be able to add the "mitsubishi" tags

Sorry I don't know if there's anything required on the Keyence side to make this work. We don't have any Keyence PLCs yet, that this works has only been reported to us by other users.