Is there a limit to the size of the tag path array that can be passed into the system.tag.queryTagHistory function? I have a query that seems to work fine up to 2096 tags, as soon as I perform a query for 2097 tags I get strange results (all zeroes for my aggregated data). Here is a snip of the code:
queryPaths = tagPaths #List of tags in a list, seems to work fine up until the list is >2096
queryAggregation = 'Count'
queryColumnNames = tagPaths #List of tags in a list
queryReturnSize = 1 #Return 1 aggregated value
queryResults = system.tag.queryTagHistory(paths = queryPaths , startDate=startDateIn, endDate=endDateIn, returnSize=queryReturnSize, aggregationMode=queryAggregation, columnNames=queryColumnNames)
Any errors in the gateway logs about exceeding message size limits? In your async thread, can you confirm the list is as long as you expect it to be and has all the paths you expect? If you set tag-related loggers to TRACE, can you see the paths you expect being output? Maybe the tags.history.query.dataloader logger, specifically.
Yeah, it looks like I'm hitting a limit on parameters (2100). Sounds like @pturmel was on the right track. See the top line of the logs below.
For some insight/clarification:
Where does this limit come from? For example, is it from the driver that the system.tag.queryTagHistory function calls automatically?
Is there a way around it?
Any other thoughts?
com.microsoft.sqlserver.jdbc.SQLServerException: The incoming request has too many parameters. The server supports a maximum of 2100 parameters. Reduce the number of parameters and resend the request.
at com.microsoft.sqlserver.jdbc.SQLServerException.makeFromDatabaseError(SQLServerException.java:265)
at com.microsoft.sqlserver.jdbc.SQLServerStatement.getNextResult(SQLServerStatement.java:1662)
at com.microsoft.sqlserver.jdbc.SQLServerPreparedStatement.doExecutePreparedStatement(SQLServerPreparedStatement.java:615)
at com.microsoft.sqlserver.jdbc.SQLServerPreparedStatement$PrepStmtExecCmd.doExecute(SQLServerPreparedStatement.java:537)
at com.microsoft.sqlserver.jdbc.TDSCommand.execute(IOBuffer.java:7417)