Logix Driver Bad Quality Tags

Hi,
I am using OPC-UA server with rockwell control logix version 24.

i am using trial linux virtual machine from inductive automation for development.

HoteIP: 192.168.2.1
Timeout 5000
Max Con. 10
Slot: 0
Automatic rebrowse : yes
CIP con. 500

Frequently all the tags are showing bad quality …

What does the diagnostics page for that device look like? Is the load factor over 100%?

If so… try some of the steps outlined here: Device Load Factor

Since you’re using it for development, I’m assuming you’re making constant changes to the PLC? If so, turn off “Automatic rebrowse” and manually restart the OPC-UA module when you create tags that Ignition actually needs to read.