I HAVE A REAL VARIABLE IN A SCHNEIDER M580 PLC AT ADDRESS %MW200, WHEN I CONFIGURE the address IN THE ignition I CONFIGURE IT AS real TYPE (HRF200) BUT IT DOES NOT READ ANYTHING AS I SHOULD CONFIGURE THE ADDRESS? ONE BYTE LESS 199
{ Please don't shout. ALL CAPS is shouting. }
Also check if you need to use the swap words setting in the driver.
I'm sorry, I did the big endian to little endian format word conversion when using DINT variables but it didn't work with real ones
Excuse me, where do I set that?
Log into the gateway web page > configure > Device Connections > Edit > check Show advanced properties..
I made the change and now I read the values of the variable, although there is a slight difference,thanks
I corrected it, thank you very much