Today, well tonight actually, we had a major incident that reduced the connectivity from gateway to PLC’s.
Unfortunatly it filled the entire logg, so I can not go to the root cause. I think. But I did found this;
No optimized AddressBlock list found for items: [com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@5d2b7cf, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@54d38421, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@133810ef, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@1dd6b9a3, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@daa1919, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@45906601, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@167ca934, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@3ecf01f9, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@63f0b5e8, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@251677f9, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@56504f66, com.inductiveautomation.xopc.server.addressspace.contexts.WriteContext$PendingDriverWrite@10d64c9c]
Can somebody give me an explanation what this is about?
You are correct, we also suspect it to be connected to the Siemens driver. I am planning to update tomorrow afternone when the plan is not operational.
I am thinking the same thing. But I do not recall working on any script. Neither does my colleague.
Are the scripts “numbered” by any way in Ignition so I can start looking for anything specific? Letts just say there are a lot of scripts running…
I found the issue, the tag connection to an transaction group was wrong. Actually it was double to the same tagg.
None the less I am updating to Ignition 7.9.16 tomorrow. I have noticed small buggs like not being able to cancell a report while it is running and so on. Maybe these smaller issues in the gateway are resolved.