I have successfully connected and mapped modbus address from a Allen bradley Micro850.
The issue that i am having is not all mapped tags are being carried over. i have 40001 to 40026 Reals that i have mapped. ( see pic) when i set it up in Ignition i am only getting (12) of the tags coming through. "Subscribed" as soon as i subscribe to the 13th tag they all get bad quality tag.
I have been able to map and use in the design editor of the tags that come through.
but not the rest of the tags i want to use.
how do i get a larger amount of "Real""Float" tags to come through?
Interesting.
is there a better way to set this up?
it's literally connected to the the Ignition PC. on the same gateway address. no other slaves or middle man pc or PLC.
Thanks. for your input. i will start a service ticket for my issue.
You're mixing up the underlying Modbus addresses and the purpose of the start/end in the mapping.
It looks like you should start/end at 0/12 or 1/13 (it's superficial, just determines display name and tag count).
Forget the Ignition Modbus mapping page exists. Manually create OPC tags using the syntax described in the manual. This way you know exactly how many tags you have and exactly what Modbus address they are at.