Information as below
- Ignition Version: 8.1.23
- Issue: Socket connection closed every 30 minutes
- PLC: Allen Bradley Micrologix 1400
We did the ping testing at same time, there is no network issue. If expert have any idea, please share your experience with me, Thanks.
Details:
1 Like
Connection reset is coming from the ML1400 itself, or perhaps from a firewall along the path. Some firewalls don't like long-duration continuous connections. 30 minutes sounds suspiciously like a firewall timeout.
Using wireshark between the PLC and its network switch, and simultaneously between Ignition and its network switch, would provide a definitive answer.