During the presentation, the ease of moving an existing Ignition Gateway to Maker Edition was simplified a bit too much for this initial release. We are working to make it that simple in 8.0.15, but the current steps to migrate are as follows:
- Make backup of your existing Ignition gateway and shut it down
- Create new install of Ignition specifying Maker Edition and go through the commissioning process. Some things you want to be aware of:
- We advise renaming the service when using the new installer
- If you want to use the same install location, you can rename the existing Ignition install folder.
- At this point Maker edition should be installed and licensed.
- Shutdown Ignition
- Open data/ignition.conf and remove line that looks like wrapper.java.additional.4=-Dedition=maker making a copy of the line for a later step.
- Start Maker edition version, it will look like standard Ignition at this point
- Restore your Gateway backup and let Ignition come all the way up
- Shutdown Ignition
- Open data/ignition.conf
- Add line wrapper.java.additional.4=-Dedition=maker back making sure to adjust the number before the equal symbol to a value that doesn’t already exist and save the file
- Start Ignition