Good afternoon for everyone,
I’m using a PLC Micro 850 and I adressing it in ignition via Modbus TCP and the gateway mentions that the PLC is connected. But when I try to address a PLC tag in Ignition it always appears that the tag value is bad.
I have already verified that the tcp address of the PLC and the ignition tag match. Example: a Boolean address in the PLC has the address 000001 and the OPC tag Path of the editor tag I put the following: [PLCName]C1
I hope, that can you help me with this issue.
Have you tried configuring that modbus address to be a coil for the type? If you share your modbus address mapping, it might help figuring out what’s going on.
And the modbus mapping on that device in the Ignition Gateway has C1 defined as a coil in More → Addresses?
Defining the address map isn’t necessary, C1 is a valid Modbus address on its own.
Try specifying unit/slave id 1 by using 1.C1 as the address,
The address used 1.C1 works. Thanks for the help