Hello all, I am trying to read the temo via modus from IDEC PLC.
The HR registers are giving me data but its a multiplier of 10.
The image shows 750 as the output but in reality it is 75.0F . How do I convert it ?
Hello all, I am trying to read the temo via modus from IDEC PLC.
The HR registers are giving me data but its a multiplier of 10.
Hi,
Use tag scaling.
For your use case, you need to set the following:
Scale mode: Linear
Raw Low: 0
Raw High: 100
Scaled Low: 0
Scaled High: 10
The default settings should be enough.