Modbus Device status in Tag
Dear all,
I have few Modbus TCP device.
Those are communicate with Ignition Gateway without problem.
I just would like to have the status of “connection” from my Modbus device in a tag , to make an alarm when the “communication” is broken.
Could you help me to tell me how can i do ?
Regards
Olivier
Check out inductiveuniversity, it should show you how to do what you want and more.
Sorry,
I Explain : I have no problem to make an alarm with a tag.
My problem is , i haven’t found in the system tags , the status “connected” from my 8 Modbus Devices.
( Those status i found in the Gateway OPC-UA SERVER/Devices/ status (from Modbus TCP)
Did you manage to find an answer to your problem?
I would be needing the exact same thing :wink:
Thanks for your help !
When you add device to OPC server you should get a tag structure like so. modbus
These tags are always in “Bad_Stale” :
But on the gateway Opcua Devices webpage, I’m able to see the correct status:
I’ve tried using script to fill a power table with the device status:
event.source.parent.getComponent('pwtDeviceStatus').data = system.device.listDevices()
And this is working well:
But I still don’t know how to create an alarm based on the state being different than “Connected”.
It’s all good, my mistake was that the “default” tag group was deleted, so the tags were not subsribable.