Hello,
Having a Modbus read error issue. Using a flow meter connected to a CommField RS485 to Modbus TCP converter. DVS-485-2.
I may have the incorrect addresses, but would that prevent a response?
Inbound and Outbound port 502 open.
Any help would be appreciated.
Thanks!
Jeff
Often, yes.
Try unit ID 1 instead of 0.
I'd also recommend you don't use the address mapping at all; just create OPC tags using the address syntax outlined in the manual.
Your screenshot clearly identifies this as a core certification test. Getting help for such on the forum is forbidden.
1 Like
Already turned my test. This is for an unrelated problem. But I appreciate the concern! I'll change the name of the Gateway : )
Jeff
1 Like
I'll be remoting in on system that my questions are based on soon. I'll try your suggestions. Thanks!