Modbus RTU devices conflicting in Ignition Designer
I am trying to connect two devices to Ignition in the following manner. Device1 and Device2 are daisy-chained on the same RS-485 network. This RS4-85 cable comes back to a MOXA N5232i Serial to Ethernet converter and is connected to our network switch via a Cat5 Ethernet cable. I have double checked the wires on the RS-485 network, the IP address of the MOXA I am communicating with and the Slave Addresses of Device1 and Device2. I am using the Modbus RTU over TCP module to connect to these devices in the gateway and I have created a UDT with corresponding tags for these devices in Designer. I don't know why but the Designer seems to read only one of these devices at a time and the other one shows a red connection. "View Tag Diagnostics" simply says "Bad Not connected, Value should be received from another variable" and then randomly reads the right value and then goes right back to red. I have used these MOXAs with other devices in my facility over the same configuration and it works just fine. The cables have been checked twice as well for any damage or otherwise and appear to be perfectly fine.
Any help diagnosing this issue would be fantastic.
Thank you. :slight_smile:
See screenshot below.
If they are on the same physical circuit, then they are required to have distinct slave unit IDs, and you must use a single Ignition device definition to talk to them. There can be only one master on an RS-485 channel.
Yes, sorry I didn't make that clear. Both these devices are on the same physical circuit but my Ignition server is only communicating with the MOXA. There are separate slave unit IDs for both devices
Right, but you can only make one Ignition device for the whole channel. Then use the separate unit IDs within the single Ignition device. Did you do that? (There can be only one connection from Ignition to the TCP+RTU port on the Moxa.)
Yes I did. There is only one device in the gateway. This is the device name in all my tags and the different tags use different unit IDs
Try turning off the "Reconnect After Consecutive Timeouts" setting on the Ignition device configuration.
If it's still an issue with that turned off then share some logs.
I made that change as described on the device in the ignition gateway. Now the values for either tag do not update, just flash between red and black in the designer. Nothing in the reference log for either tag.
You could try grabbing a wireshark capture and/or slowing down the poll rate.
Hi Cody,
Did you find a solution? I’m having the same issue. Two identical devices on the same RTU network one master, ID are set to 1 and 2 in ignition, and devices themselves are set to drop numbers 1 and 2 for the network. If I delete one or the other from designer, value (coms) work fine, but if both are setup in designer, value’s flip black from (good) to red (bad). Baud rate 19200 8N1. estimate 900 tags on each device.
Modbus RTU is a single-master protocol. If you make two devices in Ignition to scan different drops on the chain, the masters will interfere. You have to use a single device in Ignition and use the unit prefixes in the OPC Item Paths to distinguish the drops.
Other notes:
  • The spec for RTU requires either parity or two stop bits, for a character frame 11 bits long.
  • 19200 baud will transfer <860 16-bit registers per second, presuming all are packed together in memory (no gaps, all requests get 125 words).
You might just be trying to go too fast.
Hi Phil,
I appreciate your quick reply.
I do only have one master on the Device Connection (Modbus RTU) with one address configuration page for two devices (ID1 and ID2).
Still having the same issue when trying to read or update values on more than one controller. I've tried just about everything I could think of. These are Danfoss EKE400 Evaporator controllers. One controller has about 50 gaps in the Modbus addressing (610 tags) , so two controllers >100 gaps and 1230 tags. All those gaps don't help anything. All addresses are Holding Registers (INT16). I'm an engineer here at Danfoss. I did not develop the application on these controllers specifically, but I have others, and I try to make all registers contiguous. I've tried lowering the baud rate, tried 8E1 parity, tried 'span gaps' in ignition, and lowered consecutive reads from 125 to 3, tried 120Ω resistor(s) but nothing seems to help. Question though: What exactly is 'STEP'? And is it necessary? It doesn't seem to do anything checked or unchecked. Also, Is there some other setting in Ignition that you could suggest I try?
(attachments)
EKE400_modbus-config_UnitID1_UnitID2_20260113_1331.csv (3.99 KB)
I don't ever use the address mapping feature, and IA recommends not using it. It is very hard to correlate network traffic with OPC tags when using it. Instead, just make OPC tags in Ignition with manual OPC Item Paths. Some example item paths:
[device]1.HR17702
[device]1.HR17703
[device]1.HR17736
[device]1.HR18102
[device]1.HR18103
[device]1.HR18110
[device]2.HR1901
[device]2.HR1902
[device]2.HR1903
[device]2.HR3001
[device]2.HR3002
[device]2.HR3022
I don't know if you are using one-based or zero-based addressing.