Modbus Tag Adressing for Longs and Shorts
How should I address long and short Modbus addresses in ignition for OPC Tags?
Modbus Address Examples: 400467 L
400470 S
400469 S
400461 L
400463 L
So for 400467L, would the address be [DEVICENAME]HRL467?
For 400470, would the address be [DEVICENAME]HRS470?
Shorts are 16-bit, so just [Device]HR470 etc…
Longs are 64-bit, so [Device]HRI_64461 etc… (yes, the syntax is ugly because the “64” runs into the address)
The address syntax is documented here: Modbus Addressing - Ignition User Manual 8.1 - Ignition Documentation
I implemented the prettier "HRL" syntax (and HRUL) in my Advanced Modbus Driver.... (: