Hi,
I’m having issue pulling modbus data into Ignition. Using Modpoll I am able to pull the correct data from the Modbus gateway using the following command.
modpoll -t4:float -f -0 -r 16 -c 62 -l 10 192.168.1.100
-t 4:float 32-bit float data type in output (holding) register table
-f Slave operates on big-endian 32-bit floats
-0 First reference is 0 (PDU addressing) instead 1
-r # Start reference (1-65536, 1 is default)
-c # Number of values to read (1-125, 1 is default), optional for writ
-l Poll rate in ms, (1000 is default)
NOTE The addresses are half the Byte value given to me in the Modbus Address Table
MODBUS Address Table snippet shown here
The Modbus address offset is 4 Bytes (32 Bits) and Big Endian and in the holding register.
Below is the system config info the modbus gateway was given to us.
REMOVED LINK AS NEW POSTER ONLY ALLOWED 3 IMG - Will upload in replies
Using Ignition 8.1 I thought it would be straight forward to get the same data pulled over and followed the guides provided by Ignition https://docs.inductiveautomation.com/display/DOC80/Connecting+to+Modbus+Device
Below is the settings used on my Ignition Gateway in the OPC UA Device Connections.
REMOVED LINK AS NEW POSTER - Will upload in replies
Following these ignition guides I got erronious data getting pulled through Ignition, as shown below.
The tags were written like below.
REMOVED LINK AS NEW POSTER ONLY ALLOWED 3 IMG - Will upload in replies
[Radial_Forge]HR56 & HRF56
Even tried this forum post https://forum.inductiveautomation.com/t/modbus-read-two-register-into-one-opc-tag/41858
REMOVED LINK AS NEW POSTER ONLY ALLOWED 3 IMG - Will upload in replies
I believe I must be doing something stupid or missing one vital step. If anyone is able to help me it would be greatly appreciated!
Thank you,
John