The address table appears to suggest they are zero-based. Ignition’s driver defaults to one-based. Change that setting on your device. Your OPC item path would be [Radial_Forge]HRF56
. You might also want to play with the swap words setting.
You may also need the node number. Like [Radial_Forge]1.HRF56
.