Version : 8.1.24
In Gateway ,I add modbus tcp device and connect local Modbus Slave Tool.
OPC UA Modbus Config:
Modbus Slave Config:
Then in the OPC Quick Client, I subscribe tag can read its value ; but I read tag ,show bad.
Opc Quick Client:
Version : 8.1.24
In Gateway ,I add modbus tcp device and connect local Modbus Slave Tool.
OPC UA Modbus Config:
Modbus Slave Config:
Then in the OPC Quick Client, I subscribe tag can read its value ; but I read tag ,show bad.
Opc Quick Client:
Modbus TCP tags switch to bad quality - Ignition - Inductive Automation Forum
It’s probably the address offset, not the DataType. Try turning the “Span Gaps” setting off.