Modbus TCP SOCOMEC

I have a Socomec Diris a40 power monitor and have made a connection to it.
I am having issue reading the registers as the manual states addresses 50512 to 50586
Anyone successfully got data from similar?

By any chance, Were you able to get this going?

What's happen exactly?

Here there are some ideas to solve this issue.

  • Span GAPS in driver configuration
    or
  • HR450512 <-- ADD '4' in front of register

Yuck. I've worked with at least 10 different brands of power meters, and socomec are the worst for getting data out of.

A previous integrator on a project I currently work on has defined registers of e.g. HRF345 for active power phase 1.

Good luck.

Definitely never this.