Modicon Momentum PLC Conectiong and disconnecting

We have Modicon Quantum’s and Momentum PLC’s in our facility. I can connect (and stay connected) to the Quantum’s. I’ve tried 3 Momentum PLC’s and the status on the Devices page constantly show “Connected” and then 4-5 seconds later “Disconnected”. It continues to change status until I delete the connection. I’ve gone through the Advance settings Enabling and disabling each one to see if any would have an effect on the connection stability, nothing changed. I tried setting up the ModBus RTU over TCP…that didn’t work either.

I didn’t try setting up tags as I’ sure this should stay stable in the “Connected” state.

Any one have any ideas?

Have you subscribed to any tags on it yet? Most Modbus devices will close inactive TCP connections, while Ignition’s drivers will keep reconnecting.