More issues with Emulate connectivity
I know this is not the first time this topic has come up, but I cannot get Ignition device connectivity to an Emulate slot. I have done this successfully on other machines, but on this VM I cannot get out of ReconnectWait status. Does anybody see anything in the attached config that is wrong? I replaced “localhost” with the IP address in the Hostname and it doesn’t fix it. OPC Quick Client also does not see the device.
You need to use the OPC-COM driver and connect to the OPC topic you setup in RSLinx. Have a read.
Also, you might be able to use FactoryTalk Linx and make an OPC-UA connection since that is a OPC-UA server. I have not tried it, but maybe someone on the forums has.
Not necessarily, see this post, Connecting to Allen Bradley simulated plc.
@pdixon saw that post, he was the last to respond. I'm not sure why it's not working for you.
Well, this is news to me. Just tried it, worked. Sorry OP, I've got nothing...I'll see myself out.
I just noticed today @Travis.Cox made a L5K parser, I think it’s been out for a while though.
Download here:
Not a fix to your issue necessarily, but a way to test nonetheless.
You can also dump your Logix project into my Ethernet/IP module if you don't need emulation of the ladder logic.
Thanks Phil, but I need emulation; I need the logic to run and operate
For an example, this is another VM that I have. Everything works. I don’t see any difference between the 2 VMs or my configuration.
This shows the device configuration for SheetTest, which I am using to connect to a slot in Emulate. I am using Flintium objects configured for the SheetTest OPC device
This shows that I successfully connect
This shows what it looks like in runtime. My Ignition application is able to connect the Flintium object and faceplate to the running logic in Logix.
I am now trying to do the same thing in another Win10 VM. I cannot get the device to connect to my Emulate slot.
Ah, more important info. If you have one VM working, and the other isn't, that's obvious to me that there is something different between the two of them. Screenshots really aren't going to help much.
We narrowed it down. We setup trace level logging and found a connection refused:
io.netty.channel.AbstractChannel$AnnotatedConnectException: Connection refused: no further information: /192.168.148.4:44818
java.net.ConnectException: Connection refused: no further information
I assume this is a security level thing in Linx, but not sure where
Port 44818 is the Ethernet/IP port, not an OPC/UA port. Are you using the Logix driver (Ethernet/IP) or are you creating a separate OPC/UA connection?
If the former, have you told RSLinx to bind the local Ethernet/IP port?
Logix driver. It is a connection refused issue, which implies security (see above). I have never had to bind an ethernet port in Lix to make it work; other VMs work without having to do anything special in Linx. The Linx Gateway configuration (see screenshot above) looks correct
Can’t you just use the other working VM?
No. The whole point is to get this working on the VM with the Rockwell licenses that are authorized on this VM
It has been a while, but this is still an issue. It looks more like an Ignition configuration issue. Notice in the attached image I have 2 test clients successfully connected to a tag in the emulator, but Ignition still cannot connect. If the problem was on the Rockwell side, neither OPC test client would be able to connect. The fact that OPC test clients can connect but Ignition cannot suggests there is an Ignition configuration problem
Only if you consider the configuration problem to be that you're using an EtherNet/IP driver connection from Ignition and an OPC (Classic?) connection from those clients... entirely different methods of connecting.
Thanks for the reply. What I don’t understand is how it works on my other VM, as shown on Jul 9. I don’t see any difference in the Ignition config
Sorry, I've never tried to set up a direct connection to an emulated PLC using the driver, so I don't have any helpful suggestions. Last time I looked at this it wasn't possible.
Your error from the 10th is a pretty standard networking error. Usually either firewall or the other end simply isn't listening or accepting connections on that port.
What is the recommended method for connecting to Emulate? I have always used this method, but the VM that I currently have licensed is not working. If there is another method for connecting to Emulate, is it documented?