I have 2 env TEST and PROD.
In TEST env: 2 redundant gateway and another gateway connected with GAN, and a DB
In PROD env: 2 redundant gateway and another gateway connected with GAN, and a DB
IP addresse are different in both env.
OPCUA client are différent and some change on devices.
I would like to update PROD with gateway backups from TEST and a restore operation.
Is this a possibility in 8.3, or do we have to wait for the 2027 version, which will include partial backup and restore?
- TEST gateway have less memory than PROD gateway.
ignition.conf is different.
- Redundancy settings are different (master node address) redundancy.xml file is preserved ?
- Gateway network for redundancy or for other gateway communication
trusted cert are not the same ?
- opcua client connection
With gateway mode ENV = TEST or PROD I can manage DB for example connection change but is it possible to use this for other settings ?
Do I have to copy some data from PROD env to TEST env and associate them to env mode PROD to be able to restore a TEST env gateway backup to PROD ?
I'm looking for best practice to update PROD env without having to change lots of parameters each times...
I wouldn't advise the backup/restore route, but this can be pretty easily managed today by making use of VCS. You'll need to trigger a config scan on the PROD Gateways after the placement of the resources in question, but you can get where you're trying to go today without waiting for the partial import/export feature in 2027.
Ok, I see,
Our Ignition 8.3.9 gateways have no internet acces, VM (no docker) and the backup seemed like a good way to update PROD gateways from TEST gateways.
When we want to restore a backup in PROD, I think that the issues are the Following files:
- ignition.conf
- gateway.xml
for redundancy.xml, the doc mention:
Notably, when restoring a Gateway backup on an existing Gateway, the following items are not changed or replaced by the backup:
- Modules
- License information/grants
- Tag Reference Store
Trusted cert are in the data\config\local, I think that restoring a backup doesn't change them ?
@paul-griffith could confirm ?
Other settings should be well managed with deployement Mode...
But ignition.conf will receive the deployement Mode value of the TEST env !
If I undestand correctly the other solution your mention is to copy:
- Ignition\data\config from TEST gw to PROD gw
(with settings according a deployement mode, for example core = PROD and TEST)
- Ignition\data\projects from TEST gw to PROD gw (or project import)
and do a gateway scan (and projects scan if necessary)
You can have ignition.conf include a supplemental file that is outside the data folder, so it doesn't get included in any backup. Do this, with same name, in all environments. Have the deployment mode setting in this external file, and it won't be broken by a gateway restore.
Clever for ignition.conf
I hope ignition would not try to modify the file on upgrade.
I don't known if there are some solution for gateway.xml and if this file is always replaced when restoring a backup with the one in the gwbk....