Native database redundancy (replication / resync) in Ignition – current status, roadmap, and recommended architecture
Hello,
We are a system integrator in Korea building data center EPMS/BMS/DCIM systems on Ignition. Our sites run a Redundant Gateway Pair (Master/Backup), and our customers increasingly require the database layer to be redundant as well, with no data loss.
Environment
  • Ignition version: [8.x.x]
  • Database: [MS SQL Server / PostgreSQL / MySQL] [version]
  • Architecture: Redundant Gateway Pair, [N] tags, history rate s
  • Data stored in DB: Tag History, Alarm Journal, Audit Log, Transaction Groups, Script/Named Query writes
Our current understanding (please correct us if anything is wrong)
  • Ignition does not natively replicate or synchronize data between databases; DB HA is expected to be handled by the RDBMS.
  • Failover Datasource (STANDARD/STICKY) only reroutes queries to a secondary connection and does not resync data back to the primary after recovery.
  • Tag History Splitter duplicates Tag History writes only; Transaction Groups, scripts, etc. are not covered.
  • Store & Forward buffers history data while the DB is unavailable.
Questions
  1. Is native database redundancy (replication or automatic resync between primary and secondary DBs) on the roadmap for 8.3 or later?
  2. For a Redundant Gateway Pair in a mission-critical data center, what DB HA architecture does IA recommend (DB listener only / Failover Datasource / History Splitter / a combination)? Field experience would be greatly appreciated.
  3. When using Failover Datasource or History Splitter, how should we handle data written only to the secondary DB during an outage (gaps or duplicates after fail-back)? Is there a recommended resync method?
  4. How should non-history data (Transaction Groups, Alarm Journal, Audit Log, Script/Named Query writes) be protected in this architecture?
Thank you.
For high availability I think a better way to go is always on availability group. To Ignition it's just a single point connection but covers what you want.
Thank you for your opinion.
  1. There is expected to be some form of redundancy support in the new Core Historian at some point. Not sure if it will make v8.3.
2,3,4) TigerDB has become an Enterprise Partner of IA, as announced at ICC. Their product, slated for 2027, integrates TimescaleDB closely within Ignition, though the actual database redundancy remains external. External DB HA support covers non-history DB writes as well.
I don't expect Ignition to ever be a "no data loss" redundancy platform itself--its failover occurs in seconds, not fractional seconds.
If you need data replicated between databases/high availability, do it with your database/your tool of choice.
We are never going to have as good of a solution as your database vendor, because:
  1. We're not a database vendor
  2. We are operating from the position of one or two processes somewhere inside your network.
I've successfully been using replication and HA/ failover with MySQL servers with standard replication setup, and MaxScale on top layer acting as proxy and load balancer.
Works very well. I haven't been brave enough to do the AUTO failover such that a the primary write node going down is replaced by a replica automatically.
But it is possible.
Galera is also an option for multi-master MySQL database servers, where you can have writes to any number of nodes synchronously.
The Microsoft "Always on availability groups" work very well too, but obviously way more expensive.