When I configure an OPC UA connection, under Allen-Bradley>Ethernet, there are only a few selections available (SLC, MicroLogix, ControlLogix). I set up a connection using the ControlLogix device, for a CompactLogix. It says it is connected. Is this proper or do I need to add a device driver for CompactLogix?
Also, sorry if this is not the appropriate area for this question.
For now, I think it should be fine. Check to make sure all the data comes in fine, and that you can write to all different types of tags. I believe the difference is a header packet, but Im no expert.
Unless I have something mis-configured, it does not appear to be working. I also tried to add device MicroLogix 1100/1400 (for kicks and giggles).
I am able to configure, connect, partially browse (not all information from controller comes in), and create a tag. However, once the tag is created, the status cycles through various different states, and then eventually faults the controller (yeah, weird eh?)
Unknown Sourse seems to be what is returned in all error logs associated with this.
[quote]Message [HardyTest] Connection lost due to IOException.
Quick question… You were you trying to connect to the Compactlogix with the MicroLogix 1100/1400 driver just for the heck of it. Is that right? Not trying the connect to a MicroLogix 1100 or 1400 with it were you?
I have a compactlogix inhouse and Ignition has been running for a couple days connected to it. Tags and TCP port wise there is now difference on how the Controllogix works and the Compact. It was pretty easy to setup.