Null Query Error - Binding needs "double"
Hello,
I have a numeric display, and named query binding on the value.
The error I get is :
Exception: Conversion error: query returned null, binding needs "double"
on query binding for "Main Menu.Root Container.Numeric Label.value"
Ignition v8.1.10 (b2021090812)
Java: Azul Systems, Inc. 11.0.11
and the query is :
SELECT
  Sum(loads.Size) AS Yards
FROM loads
Where
 StartTime BETWEEN :Start_Date AND :End_Date
I tested it in the query browser and got a successful result without the
Where
But that doesn't sound relevant to the error. So i'm not sure what is going on.
Thank you in advance.
I'm not sure what the problem is with the information provided but did you set the named query Query Type to Scalar Query? That will return a single value rather than a dataset.
You can demonstrate the difference by running a simple query such as
SELECT 17 AS myData
in the named query editor and test it with Query Type set to Query and then Scalar Query.
One of the first things I checked, and it is set to Scalar Query. I tried with query and still no luck.
The problem is the numeric display is red and not showing correct value.
You are using an aggregate function. Aggregate functions will return a row even if there are no rows matching the where clause. You can't use a Scalar Query mode to provide a fallback because that only kicks in when there's no rows returned.
I recommend adding an outer query to the named query that uses coalesce to provide a zero.
I tried this but I am getting an error.
SELECT
  COALESCE(Sum(loads.Size) AS Yards, 0)
FROM loads
Where
the error seems to be syntax related - AS yards, 0- says to check mysql server version
Move the AS outside the COALESCE.
SELECT COALESCE(Sum(loads.Size), 0) AS Yards
FROM loads
WHERE StartTime BETWEEN :Start_Date AND :End_Date
Thank you!
been getting rusty. but gonna hop back into it with this new job.